Greg,
We had a similar issue with our 15KW PowerTech genset. The radiator fan and the blower fan (both squirrel cage types) would quit, leading to overheating and shutdown. We noticed power spikes in the 110V house lighting, which indicated that the genset was about to overheat. We managed to mitigate this by manually shutting down the genset after the power spike, and sometimes it would run fine through the night upon restart.
When the problem became too frequent, our PowerTech dealer diagnosed it as a faulty voltage regulator on the back of the control panel. To access the panel, you’ll need to pull out the genset, crawl underneath the coach to the access panel, remove it, and then climb in to remove the panel cover and expose the regulator. It’s a $250 part, unfortunately.
Good luck, and I hope it’s something different from our issue.